annoying light flicker when heat pump starts up
annoying light flicker when heat pump starts up
by eisensms » Tue Oct 13, 2009 12:27 pm
My Geothermal Heat Pump [Waterfurnace Model EW042R1SSA] causes an annoying light flicker and some noise when it starts up. Can I do a retrofit to remove this issue?
http://www.waterfurnace.ca/Engineer/IntelliStart/IntelliStart%20Sales%20Sheet.pdf
http://www.waterfurnace.ca/Engineer/IntelliStart/IntelliStart%20Sales%20Sheet.pdf
Re: annoying light flicker when heat pump starts up
by bob350 » Tue Oct 13, 2009 1:28 pm
Interesting. This also appears to lessen the required size of a generator during a power outage.
Re: annoying light flicker when heat pump starts up
by teetech » Tue Oct 13, 2009 1:35 pm
Assuming there is not a problem with EW electrical, this should solve your issue. The Intellistart is a soft start device designed to cut your LRA by 60%. It can be installed any unit with a scroll compressor, 2 stage or single stage. Age should not matter.
Re: annoying light flicker when heat pump starts up
by Looby » Tue Oct 13, 2009 7:51 pm
Thanks, looks like a winner. Any idea on pricing?
Re: annoying light flicker when heat pump starts up
by eisensms » Wed Oct 14, 2009 2:08 pm
Well, let's order two and split the cost, OK?
Re: annoying light flicker when heat pump starts up
by engineer » Wed Oct 14, 2009 8:09 pm
Looks promising.
I'd like independent corroboration of reduced amps. If the thing works as advertised it could save thousand$ of standby generator dollars.
My own Waterfurnace has a nameplate LRA of 82, which contributed to my selection of a 24 KW 1800 RPM standby generator. After that 82 LRA spike my WF settles down to using 6 amps in cooling, 8 amps heating in low stage.
The 6 amp WF hits the generator harder (judging by ear) than my 5600 Watt clothes dryer...
I'd like independent corroboration of reduced amps. If the thing works as advertised it could save thousand$ of standby generator dollars.
My own Waterfurnace has a nameplate LRA of 82, which contributed to my selection of a 24 KW 1800 RPM standby generator. After that 82 LRA spike my WF settles down to using 6 amps in cooling, 8 amps heating in low stage.
The 6 amp WF hits the generator harder (judging by ear) than my 5600 Watt clothes dryer...
Re: annoying light flicker when heat pump starts up
by flynmoose » Sun Nov 01, 2009 8:02 pm
Anyone order one of these yet?
I'm definitely interested and am curious about cost and results.
I'm definitely interested and am curious about cost and results.
I keep looking
by Mark Custis » Mon Nov 02, 2009 6:14 am
For Copeland to mate a Scroll compresor to an ECM drive.
- Mark Custis
- Industry Professional
- Posts: 1224
- Joined: Sun Jan 11, 2009 12:25 pm
Re: annoying light flicker when heat pump starts up
by teetech » Mon Nov 02, 2009 6:41 am
Variable speed compressor will be the next big leap for GEO.
I have installed intellistart and would recommend it for cutting LRA. Also a relay and capacitor from Copeland (sized for your compressor) would help.
I have installed intellistart and would recommend it for cutting LRA. Also a relay and capacitor from Copeland (sized for your compressor) would help.
Re: annoying light flicker when heat pump starts up
by flynmoose » Wed Nov 04, 2009 7:22 pm
Anyone willing to quote ballpark for what retrofitting a Intellistart onto a Synergy3 system would run (parts & labor)?